UPS doesn't last long

Status
This thread has been Locked and is not open to further replies. Please start a New Thread if you're having a similar issue. View our Welcome Guide to learn how to use this site.

associates

Thread Starter
Joined
Jan 16, 2007
Messages
17
Hi,

I was wondering if anyone might be able to help me here. I'm looking for a better UPS for my network. At the moment, i have a UPS called Powerware 3110 that connects a server, a PC and 2 routers. but it doesn't work the way i wanted it to. Yesterday, we had a power blackout in our area. It kept the server and the rest of the network running for less than 2 minutes when the sudden power blackout started. I dont think 2 minutes would be enough time to shut down the server and the other PC properly. Consequently, both server and PC were shut abruptly because of no more electricity running through. I was told that it may be because the server and the other PC draw too much power out of the UPS and it's true. I tested it. I unplug the server and the PC from the UPS and just left the routers connected to it. Then, i played the switch on the UPS on and off. It still gave a bit of power to run the routers and modem for a few minutes before it died.

My question is if there are anyone who might have had the same experience and would like to share their ideas as to overcome this issue, I'd be very grateful.

Thank you in advance
 
Joined
Dec 17, 2005
Messages
317
that unit is good for one pc, monitor.

putting the load that you did on it uses all its
capacity in a few minutes or overheats
and shutdown in a few minutes.

get another unit for the server.

you want to have the ability to safely shut
down your system and not loose data.
so run just your pc and monitor off the
battery. run things like printers through
the surge protection but not the battery.
you get about 15 minutes time or less
depending on your system load, you want to
size your ups to get about 10 or 15 minutes.
 
Joined
Aug 26, 2005
Messages
894
Powerware 3110 is 650-700va. You're probably exceeding that. Most deskop manufacturers shoot for 5-10 minutes of runtime at load.

Generally you don't want a lower load ratio than 1.3:1. (That is ration of VA drawn per VA of capacity)

Look at the power ratings for the equipment you plug in. Real quick and dirty PF determination is volts * amps (which gives you watts, which for this purpose is close enough for volt amp calculations)

Add up your VA rating for all of the equipment that you're running off UPS. Divide VA capacity of UPS by summed VA of equipment connected.

Example:

Powerware 3110: 650va capacity.

Desktop: 3A @ 110V = 330va
Server: 5A @ 110V = 550va
LCD monitor: 1.5A @ 110V = 165va
Wireless router/etc: 1A @ 110V = 110va

SUM: 1155va

UPS capacity (650va) / load estimate (1155va) = load ratio of 0.562:1

OOPS! You've cut your UPS runtime by at least half, if not more. On a larger scale, this would cook the inverter/rectifier in the UPS.

The moral of the story is to add up your capacity needs and find either multiple UPS to split the load across, or purchase a larger UPS. (Of which, you'll find that you will probably only be able to find a 1100-1200va UPS that will run off a 15A 110VAC circuit)

Hope this helps.
 

associates

Thread Starter
Joined
Jan 16, 2007
Messages
17
Thank you all for your replies.

Now, i'm getting to know what i'm doing here. Yes, it allows 650-700va capacity. However, if i may ask one more question. Is this for the whole unit?

I mean I can see that the powerware 3110 provides 5 sockets for "continuous surge protection". Three of them are for "Battery Power Backup". Just want to check if I do the right thing here. If i were to use this UPS for the server only (since it can only support one PC), I could connect one socket of "Battery Power Backup" to the PC Box, 2nd socket to the monitor. Is this right? sorry for asking this silly question but i just don't want to get into unexpected problem again. This would leave me one more socket of "Battery Power Backup" and i can connect it to something else so long the total amount of loads does not exceed 650VA.

Thank you in advance
 
Joined
Aug 26, 2005
Messages
894
Yep, I have a Liebert UPS that's similar. 3 of the outlets are powered by the inverter, and 3 are simply powered by the surge protector.

The VA rating is only for systems powered by the inverter. The other 3 outlets are parallel to the inverter, and your only limiting function is the circuit breaker or melting point of the UPS case :)
 
Status
This thread has been Locked and is not open to further replies. Please start a New Thread if you're having a similar issue. View our Welcome Guide to learn how to use this site.

Users Who Are Viewing This Thread (Users: 0, Guests: 1)

As Seen On
As Seen On...

Welcome to Tech Support Guy!

Are you looking for the solution to your computer problem? Join our site today to ask your question. This site is completely free -- paid for by advertisers and donations.

If you're not already familiar with forums, watch our Welcome Guide to get started.

Join over 807,865 other people just like you!

Latest posts

Staff online

Top